I try to communicate between SLC MVI46-MCM (master) and Trio motion MC206X (slave) in modbus protol with RS422 4 wires.
When i connect 1 trio slave, it communicate correctly (read and write). With 2 or 3 slaves, i receive many corrupted character on the MVI. The read work correctly but the write does not work.
Does anybody have experience with this device ?
Thank for your help
When i connect 1 trio slave, it communicate correctly (read and write). With 2 or 3 slaves, i receive many corrupted character on the MVI. The read work correctly but the write does not work.
Does anybody have experience with this device ?
Thank for your help
Do you have 120 ohm termination resistors at each end of the network? You do not want resistors at each device.
Bill Sturm
Abbeytronics LLC
Bill Sturm
Abbeytronics LLC
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
Automobile, n.:
A four-wheeled vehicle that runs up hills and down
pedestrians.



