Momentum/ 984/ Premium PLC's - how do I monitor the Modbus Plus link light status and Running status in WW InTouch?
PLCs and related questions. topic
Posted by K Grasty on 14 July, 2009 - 10:08 am
I had a situation where the program on a PLC program was not running, but my IO status thought the communications were 'good'. I would like to know:

(1) if there is an internal register in the PLC that stores the status of the PLC program - ie: Running/Not Running.

(2) if there is an internal register in the PLC that stores the status of the PLC communications on Modbus Plus as well as ethernet.


Posted by Harvard on 15 July, 2009 - 10:44 am
The most common method of making a "Watch Dog Timer" is to have a Modbus register continually increment and roll over controlled by the PLC program. Then the Host monitors that Modbus register to ensure it is always changing.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.