Reading Mettler Toledo IND 780 weight on TSX 57 PLC using Ethernet
PLCs and related questions. topic
Posted by Chimwana on 13 October, 2009 - 9:46 am
Would you please assist how I can setup my IOscanning to read IND 780 data stored in modbus registers like 400001.


Posted by Robert Willis on 14 October, 2009 - 12:04 am
It would help if you provide us with the details of which programming software you are using (PL7 or Unity Pro). In general you configure a entry in the I/O Scanner table that will point to %MW1.

%MW = "Memory Word"
1 = First %MW Reference which is equivalent to Modbus Register 400001, 40001, 4001 etc....

The I/O Scanner will allow you to configure both a Read and Write at the same time. Provide the I/O Scanner Entry with the proper IP Address of the device and then set the Index Entry to 1. Depending on the device that you are attempting to communicate with you may need to alter the Index Entry.


Posted by Chimwana on 14 October, 2009 - 9:13 am
Hi
I'm using PL7 Pro when I'm setting my IOscanning I can not input 400001 address as my slave starting ref add. I tried to configure wonderware DAserver to be reading the scale data but I wasn't successful as well.


Posted by Robert Willis on 14 October, 2009 - 11:45 pm
I do not have PL7 installed on my computer and am going from memory.

You do not enter 400001 into the slave reference. You only need to enter 1 since the 4x reference is implied by the I/O Scanner.

When you attempt this with your HMI you will need to follow the addressing scheme that they utilize. Some HMI packages require that you utilize the entire address such as 400001 (Commonly referred to as Modbus six digit addressing) or 40001 (Commonly referred to as Modbus five digit addressing). Other software may require that you only input the offset within the 4x register area which in this example would be one.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Nerds in Control, LLC. All rights reserved.