Modbus Links
Jump to a Date
modbus.control.com/rss/
Dear Sir,
We have to communicate AB PLC Micrologix-1200 with GE Fanuc PLC PCM Module - IC693CMM321.
We require RS485 communication from Micrologix-1200. Pls. send solution for the same.
If we use PM02 Cable, One sided D type connector shall be connected in Micrologix-1200 & other side shall be connected with ADAM (RS232 to RS485) convertor.
We will use this RS 485. Kindly Reply me on my mail id:
sapan.kothari [at] advancedsystek.com
Thanks & Regards,
Sapan Kothari,
Engineer - Projects,
M/s. Advanced Systek Pvt. Ltd.,
Vadodara, Gujarat,
India
Thanks & Regards,
Sapan Kothari,
Vadodara, Gujarat,
India
This is a common challenge usually resolved by using OPC. Please visit this link to learn more about what is OPC.
http://www.matrikonopc.com/resources/opc-tutorials.aspx
Wassim Daoud
Global Solutions Architect
www.MatrikonOPC.com
Wassim Daoud
www.MatrikonOPC.com
The Micrologix supports Modbus on it's serial port....does the Fanuc unit? If so, that seems the most reasonable way to do so.
The GE Fanuc IC693CMM321 is an Ethernet module. It communicates using GE Fanuc's SRTP protocol OR Modbus TCP/IP. With Modbus TCP/IP it can be both a server and a client. Client requires programming using COMMREQ commands. Server requires no programming. However, as a server, the Modbus map for registers is non-standard. Access this link to download the Technical Manual for the IC693CMM321:
http://support.gefanuc.com/support/index?page=docchann el&id=09237d4900112007ff7cf003ad0
My suggestion would be to use Modbus TCP/IP between the two PLCs.
Drake Fink
Sr Application Engineer
GE Fanuc Intelligent Platforms, Inc.
Drake Fink
Based on Mr. Fink's response earlier, you could consider our Omnii-Comm product http://www.miille.com/266-P00-Ethernet.pdf as a solution for a connection between Allen-Bradley PLCs and GE PLCs. We support both Modbus/TCP and Ethernet/IP at the same time. We are a "server" to both protocols. We can be a client for Ethernet/IP communication in some applications. You can contact me at jmiille [at] miille.com for more information.
Thanks,
Jerry Miille
Thanks,