Using Modbus to Send Data Across to Two PLCs Belonging to Two Different Networks
Need to establish serial commmunication with two PLCs of different networks.

I am having two PLCs belonging to two different IP networks. Now there is a need to share data across these two PLCs. Which are separated by 1.5km distance. Can I achieve it with modbus over serial communication? Using fibre optic as the media?

Moderator’s Note: The author has checked GE Mark V/VI as the vendor

>two different IP networks.

Presumably, you mention RS-485 because the PLCs each talk Modbus RTU over RS-485. An RS-485 port is not concerned with IP (Ethernet) addresses.

>Now there is a need to share data across these two PLCs. Which are separated by >1.5km distance. Can I achieve it with modbus over serial communication? Using fibre
>optic as the media?

If one of the PLCs has Modbus RTU master functionality and the other is a Modbus RTU slave, then, yes, you can find commercial RS-485/Fiber Optic (or RS-232/FiberOptic) converters that will handle the hardware link, depending which serial port is available for the Modbus port.