Select Page: Previous 7 8 9 10 11 12 13 14 15 16 17 Next
Control.com topic...
Software in Automation
Topic: Communications systems and equipment.
from the Process Control department...
FIELDBUS OR WIRELESS HART INPLACE OF MODBUS
Originally posted by Grace on 4 December, 2012 - 5:01 pm
NEED YOUR INPUTS PLEASE FOR A NEWBIE
New Replies:
1) Wireless HART gateways talk Modbus. In wireless HART, HART is protocol used over the airwaves...
Topic: PLCs and related questions.
from the Forum department...
modbus TCP security
Originally posted by Tim on 29 October, 2012 - 3:19 pm
best practice to secure modbus TCP
New Replies:
Seems like an odd place to apply that sort of rule set to me. Anyway - I think you could implement...
By Lynn August Linse on 3 December, 2012 - 9:26 pm -
> You can use a managed switch like our MSM-508. This will allow you to > restrict access...
You can use a managed switch like our MSM-508. This will allow you to restrict access based on IP...
By Lynn August Linse on 1 November, 2012 - 10:05 am -
I doubt any 'switch' can do this. There are many boxes which can enable/block basic traffic based...
Being an open standard i would say is a plus here as this allows you as a end user to understand...
Assume you use Modbus TCP communication only within a private subnet. Then the ModbusTCP server...
Hello, Try openwrt, you can program any security scenario. Openwrt is avaiable for most...
Topic: Communications systems and equipment.
from the Forum department...
Watlow F4 Profile Status
Posted by jdkiesel on 3 December, 2012 - 3:25 pm
Using Labview via Modbus to control Watlow F4 temperature controller
Topic: PLCs and related questions.
from the Forum department...
How to interpret Modbus error code: EA 0B
Originally posted by Weimin Chen on 26 November, 2012 - 6:05 pm
When I poll a range of Modbus registers, I got bad response if I poll one more register than the range, even though ALL the registers are valid.
New Replies:
By Lynn August Linse on 28 November, 2012 - 9:58 am -
So it is the Digi making that code - the '80 0B' looks like a bug. I haven't actually looked at...
I dumped out the port setting parameters, and yes, slavetimeout = 1000. As soon as I changed that...
Thanks a lot for your good info! Now I got some idea about the problem: it must be the Slave...
By Lynn August Linse on 27 November, 2012 - 8:43 am -
It is easy to see where the strange response is from - check out this web page, which shows how to...
Topic: Application Questions and Problems
from the engineering department...
Floating point vs integers
Originally posted by Jim on 8 November, 2012 - 10:03 pm
Using floating point numbers vs using integers when designing a slave modbus device
New Replies:
> In designing Modbus slaves how much time should be put into avoiding using floating point in...
By Lynn August Linse on 12 November, 2012 - 10:33 am -
Floating point down in small PIC-sized devices is becoming more common. The problem with integer...
From a user point of view - I always appreciate a nice float implementation. I have integrated...
Topic: Communications systems and equipment.
from the Forum department...
Exception Code 0x06 unused?
Posted by Julian on 26 November, 2012 - 10:10 am
Not any function code supports exception code 0x06 "slave device busy"?
Topic: Local and wide area networking in factory automation.
from the software department...
Reading Data from Modbus
Posted by Daniel on 21 November, 2012 - 6:44 am
trying to develop a software which is reading out data from several modbuses
Topic: Local and wide area networking in factory automation.
from the Modbus TCP Protocol department...
Modbus TCP Protocol
Originally posted by Harrison on 13 November, 2012 - 9:41 pm
How many MODBUS TCP can connect device
New Replies:
By Lynn August Linse on 15 November, 2012 - 11:49 am -
Just a quick adder on wide-area latencies. You did not say if all 2500 devices are one a single...
Hello, I agree with Lynn August Linse. You can use traditional SAP/ERP data-logger kind of...
By Lynn August Linse on 14 November, 2012 - 10:02 am -
> Customer should receive data through MODBUS TCP in real time. > Server PC should receive...
Topic: Communications systems and equipment.
from the Forum department...
MODBUS Craziness
Posted by Wes on 13 November, 2012 - 10:40 am
Need to change ports for troubleshooting purposes.
Topic: Communications systems and equipment.
from the Forum department...
Modbus Master to Master
Originally posted by Santi on 11 February, 2010 - 2:05 pm
Modbus communication between masters (point to point)
New Replies:
Similar question plz, If I have field devices that are configured as Modbus slaves and I have a PLC...
Topic: Local and wide area networking in factory automation.
from the Signalling department...
Modbus - Plc - opc Connection
Originally posted by Savronik on 7 November, 2012 - 2:51 am
Modbus - Plc - opc Connection
New Replies:
If you do choose to go the OPC route - check out the free Ignition OPC-UA server. It includes...
Hi there, There can only be one Master, normally, on a Modbus RTU network. On a Modbus TCP...
Hi, Most people today are going the other way of using OPC solution instead of creating a...
Topic: PLCs and related questions.
from the Reliability department...
MODBUS communication and total time scan
Originally posted by VSS on 6 November, 2012 - 11:00 am
How to calculate total time scan for data fetched over MODBUS
New Replies:
Dear Patrick Lansdorf, May I get the excel sheet? It would be very appreciated, if you send it...
At 9600 baud it takes about 1 msec to transmit 1 piece of data on the wire. A request for holding...
Thanks for your Quick response. attached here more information . Baud rate:9600 Request : 32 ...
Hi, I would actually say that most influential factor is/can be the response time of the slave....
You need to provide a bit more information! Biggest factor in determining the update time is the...
Topic: PLCs and related questions.
from the Forum department...
PLC/DCS scan time sync and problem
Originally posted by alwaysontravel on 4 November, 2012 - 6:16 am
It's always a dcs/plc fight, but I need some help right now
New Replies:
What sort of Advant PLC? 70/110/200/410/450 ? 250 ms for motors is too fast and likely that's...
It should be possible to create fast and slow scans from the DCS system to reduce unnecessary...
Posted by Javad babaee on 1 November, 2012 - 11:43 am
2 question regarding getting information from master using C++ and reading analog registers at the same time (I'm using AVR)
Topic: Communications systems and equipment.
from the Forum department...
MODBUS TCP/IP on WINCC
Posted by Muhammad Shoaib Ahmad on 1 November, 2012 - 8:23 am
wincc tag configuration and Modbus TCP gateway
Topic: Computers in manufacturing; also hardware discussion.
from the Controls department...
Modbus Multidrop
Originally posted by RavinderK on 29 October, 2012 - 2:40 am
Modbus multidrop communication
New Replies:
By Lynn August Linse on 31 October, 2012 - 10:06 am -
Normally you create a simple state-machine. The slave notices an idle gap on the serial line. ...
I do not understand. Each slave is only allowed to answer to a request with slave_adr == the...
Topic: Software, including programming, OS issues, etc.
from the Electronic Equipment Testing department...
Modbus read/write (0x17) function
Originally posted by Avijit Paul on 23 October, 2012 - 4:05 am
Problem with Modbus read/write (0x17) function
New Replies:
By Lynn August Linse on 23 October, 2012 - 10:12 am -
First things first, most Modbus devices do NOT support read/write function 0x17. So can you...
Topic: Communications systems and equipment.
from the Automation List department...
Communicating with Intellisys Controller using Modbus
Originally posted by mordehy banai on 9 February, 2012 - 4:01 pm
Communicating to an Intellisys controller using Modbus RS485
New Replies:
hi all, i'm technician from Indonesia, I have intellisys controller SSR 15-100HP. i have a...
Posted by Kemen on 17 October, 2012 - 4:48 am
passive modem --- voice --- wade rtu + twido plc
Select Page: Previous 7 8 9 10 11 12 13 14 15 16 17 Next
 
 

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
"About the time we think we can make ends meet, somebody moves the
ends."
-- Herbert Hoover