Nemo D6-S Modbus parameters.

Hi I am trying to connect Nemo D6-S via Modscan 32 applications. Does any one have parameters to be selected?

I have kept following in to device.

Slave side
Address is 4
Baud 9600
Time 5

Thanks

1. Is Modbus resident in the unit?

According to the spec sheet here,
http://www.imeitaly.com/docs/NT528.pdf
the model MF1CT2 has Modbus RTU over RS232 and the model MF1CT4 has Modbus RTU over RS-485

Question
Which model do you have?

2. What hardware is needed?
There appears to be separate Interface module (pdf pg 8) in the brochure
http://www.elektro-oprema.com.hr/shared_files/ime/ime_-_mreni_monitor.pdf
a device labeled "IFD0" which claims to have Modbus RTU (485)

I don't know if the MF1 device needs the IFD0 device or not.

3. Modbus doc
The multilingual Modbus manual is here:
http://www.imeitaly.com/protocolli/PR006.pdf
English section starts on page 29 pdf
The slave map starts on page 42 pdf

Note that the registers are hexadecimal, not decimal.

4. device/slave/node ID number

You claim your unit is at slave node address 4.

Question
How do you know that? I did not see a section on configuring a slave node ID address

5. Time 5

Question:
What is the "Time 5" parameter you mention?

Thanks for your reply,

The Meters we have at site are MFC1CTJ0056.

Does it required N2 convertor? I am not sure. Just got response from site that it could communicate with Johnson Control.

Thanks,

I don't know. I'd never heard of NEMO before this thread came up.

But figuring out which, if any, protocol the device talks is Step 1.