Today is...
Monday, August 19, 2019
Welcome to the Modbus Community, about
the world's leading automation protocol.
Connecting Delta SV2 PLC Using Modbus
Connecting PLC Delta SV2 to Multimeter KAEL via ModBus RTU

Hello,

How I can connect PLC Delta SV2 to Multimeter KAEL (MULTIMET-01-PC-96) by using RS-485 ModBus - RTU??

Best Regards ..

The manual here
http://www.kael.com.tr/eng/pdfler/MULTIMET-01-PC%20eng.pdf
states on page 9 that the device can only reply with one variable per Modbus message/transaction using Function Code 03 (read Holding Register).

The RS-485 wiring has Sg (signal ground) driver lines A and B, and a terminal for TR. I suspect TR is terminating resistance, but it connects to the A driver on one slave device only. Who knows?

Furthermore, that document does not have a Modbus slave table of registers/ addresses and the associated units for the data values. I'd want to find that document before I spent one minute on anything else Modbus.

To connect, you need a Modbus Master, because these are slaves.

It appears that the manufacturer offers a software package.
http://www.kael.com.tr/eng/pdfler/MULTIMET-01-PC%20eng.pdf
You might want to see what that software does and whether it meets your needs before struggling through a Modbus implementation.

This link shows ModBus Registration Table <<

http://www.kael.com.tr/eng/pdfler/Multimet-01-PC-96%20register%20table.pdf